kingpb
Senior Member
- Location
- SE USA as far as you can go
- Occupation
- Engineer, Registered
Simple setup for discussion would be a 480Y/277V solidly grounded utility service. The facility loads are predominantly 3 phase with not more than about 20% phase to neutral loads. The BESS system is rated 480V and is furnished with, what they call, neutral forming transformers (NFT) to serve the phase to neutral load. The NFT is essentially a Y-grd/delta (High / low) 1:1 transformer where the Y side is solidly grounded.
Doing this, creates a situation where the the service entrance neutral and ground are bonded together, and there now exists another location where the neutral and ground are bonded. Additionally, if the BESS is operating in island mode, the main service conductors breaker is open, but then any ground fault could still come back on either grounds to the neutral. So the question is how to maintain compliance with the NEC by only having one location where the ground and neutral are bonded together. The only thing I can think is you have to be able to switch the main service neutral (4 pole breaker) when in Island mode which would be no different than say a standby generator, and when in parallel operations you need to be able to open the connection between neutral and ground at the NFT.
Doing this, creates a situation where the the service entrance neutral and ground are bonded together, and there now exists another location where the neutral and ground are bonded. Additionally, if the BESS is operating in island mode, the main service conductors breaker is open, but then any ground fault could still come back on either grounds to the neutral. So the question is how to maintain compliance with the NEC by only having one location where the ground and neutral are bonded together. The only thing I can think is you have to be able to switch the main service neutral (4 pole breaker) when in Island mode which would be no different than say a standby generator, and when in parallel operations you need to be able to open the connection between neutral and ground at the NFT.