--- can anyone explain briefly, ---
Everybody gfave you pretty good responses, but the specific answer is, "No - you did not give us enough information."
yes, they (the generators) are the same. ---
What we know: you have 2 generators, 20MW (or larger) operating in parallel. they can not be adjusted manually
What we don't know:
With two generators that size, there is a room full of equipment - or maybe even two rooms. Depending on the age and sophistication, there could automatic voltage regulators tied to var (or var share) controls, governors tied to kw (or kw share) controls. Governors can operate in droop, isoc, or base load. Although generally only one in isoc, the other in droop or base load.
If this is a new installation, then there are issues with commissioning, programming, wiring verification.
If an existing installation, then my first question is; Have the generators ever played well together before? If so, something broke.
--- cannot adjust the pf manually for each individual generator. ---
The simplist soltuion is one is in Isoc and the other is in droop. The paralleling contoller is not programmed to share. I'm guessing there is no front panel Manual/Auto switch or you would have seen it. If you wish to manually adjust - you will need to find the paralleling controller software switch.
--- why is the pf on smaller load higher that is 0.95 while the one with 20MW is 0.8. and cannot adjust the pf manually for each individual generator. ---
--- does that situation because of the cross current compensation. is it true that the lower MW Gen will have higher pf and when its MW near 0MW it will have pf near unity?
Two 20(+)MW generators operating in parallel is non-trivial. You really need to get the wiring diagrams, one-lines, tech manuals - and if you are living right there will be design documents explaining the operation.
worm