Islanded Generating Stations

Status
Not open for further replies.

ron

Senior Member
The clearing time is related to the available short circuit current from the source and the protective device settings. Just like any source. The islanded plant just has less available fault current, like a standby optional or emergency generator at a building.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
The clearing time is related to the available short circuit current from the source and the protective device settings. Just like any source. The islanded plant just has less available fault current, like a standby optional or emergency generator at a building.

So something like a few cycles I take it in terms of CCT. :( Do close in faults vs farther out faults make a difference? My understanding is that generators speed up for faults that are mostly reactive.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Islanded but not small. With proper governors, I'm not sure how any of the generators could speed up; isn't reactive power controlled by excitation?


It is by the excitation, but during a fault R (MWs) dip and reactive lagging power (VAR) goes up.
 