Islands - NEC 2023 210.52(c)(2)

Pillar Elec

New User
Location
Newnan, Ga
Occupation
Electrician
Does anyone have any recommendations on pop up outlets to meet the new code?

I’m seeing a lot out there and drastically different prices. I want something that is tested and approved with proper listings.

Thanks
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
As far as I know, the only one actually listed for use in countertops is the one made by Hubbell.
Others suggest theirs are listed for the purpose, but when you dig into the actual listing you typically find that they are listed as furniture power units and not for use in countertops.
 