Ergo, you can’t get electrocuted. It’s safe!I bet you can't even plug anything in there...
Sent from my SM-G965U using Tapatalk
Wouldn't even be allowed here........Ergo, you can’t get electrocuted. It’s safe!
About only place it can't go when talking about the sink is within the bowl of the sink.Isn't that outlet too close to the sink, anyway?
This apparently being a non dwelling bathroom, that receptacle possibly would never get used anyway.
Also that receptacle has a good chance of already having been there and someone decided a hand rail is required.
I'm getting to the age that the bar is more likely to be needed than the receptacle.
Isn't that outlet too close to the sink, anyway?
406.4 General Installation Requirements. Receptacle outlets
shall be located in branch circuits in accordance with Part III of
Article 210. General installation requirements shall be in
accordance with 406.4(A) through (F).
406.4 (D) Replacements. Replacement of receptacles shall comply
with 406.4(D)(1) through (D)(6), as applicable. Arc-fault
circuit-interrupter type and ground-fault circuit-interrupter
type receptacles shall be installed in a readily accessible location.
Accessible, Readily (Readily Accessible). Capable of being
reached quickly for operation, renewal, or inspections without
requiring those to whom ready access is requisite to take
actions such as to use tools (other than keys), to climb over or
under, to remove obstacles, or to resort to portable ladders,
and so forth.
It appears to be a public restroom as noted by the sign above the valve handle for
employees to wash their hands
That's what I think too; they got hit with an ADA lawsuit (or threat of one) and had to install the bar long after the bathroom was originally built or remodeled....Also that receptacle has a good chance of already having been there and someone decided a hand rail is required.
hmmmmThat's what I think too; they got hit with an ADA lawsuit (or threat of one) and had to install the bar long after the bathroom was originally built or remodeled.
One thing about this that makes me a little nervous is that behind that escutcheon plate of the grab bar are mounting screws that would have had to go into a stud: no getting away with wall anchors on grab bars. So given the location and orientation of that receptacle, it would be a miracle if one or more of the screws didn't hit a conductor. That could potentially energize that grab bar AHEAD of the GFCI and if you're an old fart like me that has to hold on to it while engaging in the business of using the facility, it could make for an exciting event......
Non dwelling bathroom has no requirement to have a receptacle. If you do have any they still require GFCI protection though.how does that change anything?
. Depending on when it was done, of course. I was called on it once years ago. AHJ couldn’t provide the article requiring it. Next code cycle included the wording.Non dwelling bathroom has no requirement to have a receptacle. If you do have any they still require GFCI protection though.
How many moons ago? I first started using NEC with 1987 edition. I think it has been fairly clear since then that only dwelling bathrooms required any receptacles. Not sure how clear GFCI protection was for non dwelling bathroom then, but seem to recall it was pretty clear by 1996 or so.. Depending on when it was done, of course. I was called on it once years ago. AHJ couldn’t provide the article requiring it. Next code cycle included the wording.