All of our facilities at work require a ground of 10 ohms or less. All facilities have the neutral tied to ground at the main power entry panels. If I'm checking a ground at one facility, is it necessary to remove power and disconnect the ground from the facility to get an accurate reading of that particular ground rod for the facility?
It seems to me if the ground is left connected to the facility, it is tied to the neutral at the power entry panel, and that neutral is tied back through the power grid to all the other facilities (which have neutral tied to ground). I would think these parallel circuits would just lower the ground reading. I ask because we have some seriously low ground readings in our records, on the order of 0-.1 ohms for most facilities, but as high as 4 ohms at others.
We can use a Vibroground to perform fall-of-potential, but have access to the AEMC clamp-on checker also. I would like the most accurate reading of the actual ground resistance at each facility. Is my thought-process correct about measuring with power/ground wire disconnected? If so, do you have a reference/procedure for such a measurement? Thanks, Mike
It seems to me if the ground is left connected to the facility, it is tied to the neutral at the power entry panel, and that neutral is tied back through the power grid to all the other facilities (which have neutral tied to ground). I would think these parallel circuits would just lower the ground reading. I ask because we have some seriously low ground readings in our records, on the order of 0-.1 ohms for most facilities, but as high as 4 ohms at others.
We can use a Vibroground to perform fall-of-potential, but have access to the AEMC clamp-on checker also. I would like the most accurate reading of the actual ground resistance at each facility. Is my thought-process correct about measuring with power/ground wire disconnected? If so, do you have a reference/procedure for such a measurement? Thanks, Mike