I would weigh it on a case by case bases, if a sub panel id fed from a SDS transformer there is no need to carry the IG back to the main service and doing so could cause a voltage on it, if a sub panel is fed from the main service panel it should have separated grounding and neutrals, and should not be a problem bonding the IG to it's grounding bar, if the subpanel does not have isolated neutral and grounding, then not only is it in violation of the NEC, the grounding has current on it, in that case and if the owner didn't wish to make this panel right then I would most defiantly run the IG back to the main service panel.