Isolated Conduit in Air
What does "Isolated Conduit in Air" mean as used in 310.73 thru 310.76.
In a 12470v installation where XLP 15kv shielded conductors (MV-105) are used for assorted feeders inside a facility, and are run in RMC, what table or section for ampacity is used?
Are conduits inside a building "Isolated in Air", or are they just conduits on supports?
If these conductors are not in duct banks, and there is something special about "Conduits Isolated in Air", then there is no specific table for an installation of 2001v and higher conductors run in conduit inside a building.
Considering this, how would the ampacity of a given conductor be figured except under engineering supervision?
Roger