A arnettda Senior Member Dec 6, 2017 #1 If a spec calls for a isolated grounding receptacle, can my grounding conductor be a plain green conductor? Does it need any special markings? Green with yellow strip.
If a spec calls for a isolated grounding receptacle, can my grounding conductor be a plain green conductor? Does it need any special markings? Green with yellow strip.
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Dec 6, 2017 #2 Nothing special needed, just needs to comply with 250.119 and you have a way to identify it from any other EGCs present.
Nothing special needed, just needs to comply with 250.119 and you have a way to identify it from any other EGCs present.
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician Dec 6, 2017 #3 It is customary for an isolated ground to be green with a yellow stripe to distinguish it from "dirty" grounds and may be a job spec.
It is customary for an isolated ground to be green with a yellow stripe to distinguish it from "dirty" grounds and may be a job spec.