Isolated equipment grounding conductor

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have restaurant in which isolated equipment grounding conductor is used. However a separate conduit just for the IG conductor is provided to the receptacle. Separate branch circuit with equipment grounding conductor and circuit phase and neutral is provided for the same receptacle.

Would code allow to have IG in separate conduit from the branch circuit or not? Looked at 250.146(D) but got confused
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Part of the wording in 250.146(D) seems clear: The receptacle grounding terminal shall be connected to an insulated equipment grounding conductor run with the circuit conductors.
Also:300.3(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway,
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with Augie It must be run with the circuit conductors. How are the normal EGC and the IG connected?
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Can’t say I’m surprised. I see a lot of bizarre installed when it comes to IG.

You may want to verify the IG ground bus is bonded. Can’t tell you how many I’ve seen connected to an independent grounding electrode.


Sent from my iPhone using Tapatalk
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
I though you were a plan checker? Are you seeing this installation in person or something on a set of plans?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Can’t say I’m surprised. I see a lot of bizarre installed when it comes to IG.

You may want to verify the IG ground bus is bonded. Can’t tell you how many I’ve seen connected to an independent grounding electrode.
How's this old one? IG connection for an IG bus in a panel. Safe to say that all of the IG receptacles weren't even grounded.
Isolated Ground connection.jpg
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Why is anyone still using IG systems in a restaurant? They are worthless and quite often not even designed or installed in a code compliant manner.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Why is anyone still using IG systems in a restaurant? They are worthless and quite often not even designed or installed in a code compliant manner.
Cut and place boiler plate specifications probably.
Aren't point of sale devices the same as they were 40 years ago?
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Why is anyone still using IG systems in a restaurant? They are worthless and quite often not even designed or installed in a code compliant manner.

Most of the dozen or so quick serve brands I build use IG circuits. McDonald’s especially makes extensive use of IG circuits. Not sure if they’re still doing this at Chik Fil A because I quit building them, but they were running all their IG POS circuits through an isolation transformer.

Most of the POS vendors will not warranty their equipment unless it’s installed on an IG circuit. We have to sign an affidavit at the end of the job stating everything is to spec.

Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Most of the dozen or so quick serve brands I build use IG circuits. McDonald’s especially makes extensive use of IG circuits. Not sure if they’re still doing this at Chik Fil A because I quit building them, but they were running all their IG POS circuits through an isolation transformer.

Most of the POS vendors will not warranty their equipment unless it’s installed on an IG circuit. We have to sign an affidavit at the end of the job stating everything is to spec.
We had a similar spec for POS equipment on a college cafeteria job. Needless to say we didn't install a single IG circuit and they never had a problem. Is there any proof that these IG systems are still actually needed or are the people paying for them getting ripped off?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
We had a similar spec for POS equipment on a college cafeteria job. Needless to say we didn't install a single IG circuit and they never had a problem. Is there any proof that these IG systems are still actually needed or are the people paying for them getting ripped off?
I recall reading that there are 3 outcomes from installing an IG system compared to a code compliant traditional system...things get better, things get worse, or things remain the same....in about equal proportions.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The way I've seen these system designed and installed over the years if a true IG system did have some benefit that was always defeated by poor installation and design. In the photo I posted in post #7 the installer ran a separate IG and EGC for every circuit in the panel and then chopped out some concrete and connected to a piece of rebar in the slab to make the isolated ground. I've also seen many installations where they just ran the IG to building steel. These systems could not have had much benefit over a standard wire type EGC.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
We had a similar spec for POS equipment on a college cafeteria job. Needless to say we didn't install a single IG circuit and they never had a problem. Is there any proof that these IG systems are still actually needed or are the people paying for them getting ripped off?

I’ll say this…… I’ve remodeled a lot of older stores that have no IG at all, and use the same equipment as new stores with no issues. They still use the same IG4700 receptacle.

My personal opinion is that they’re being ripped off.


Sent from my iPhone using Tapatalk
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I always have to laugh when they truly “isolate” the ground. Insulated ground bar back at the panel, all the IG grounds ran to it, but no actual ground ran from it back to anywhere!
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
To expand upon my earlier statement about being “ripped off”; the larger restaurant brands we work for have their own engineering teams that set the design specifications for the regional EE’s that design each project. The specification for IG’s comes from the POS vendors. I’ve never directly asked the brand engineers their thoughts on it, but without the vendor requirement, I doubt they would design that into the job. The POS vendors require every component in the system be connected to an IG circuit, which is usually 12-15 circuits per store, and about 50 IG receps.


Sent from my iPhone using Tapatalk
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
To expand upon my earlier statement about being “ripped off”; the larger restaurant brands we work for have their own engineering teams that set the design specifications for the regional EE’s that design each project. The specification for IG’s comes from the POS vendors. I’ve never directly asked the brand engineers their thoughts on it, but without the vendor requirement, I doubt they would design that into the job. The POS vendors require every component in the system be connected to an IG circuit, which is usually 12-15 circuits per store, and about 50 IG receps.


Sent from my iPhone using Tapatalk
Since you are heavily involved with building this type of restaurants I'm curious when the jobs are done and POS equipment is installed how much of it even connects directly to the receptacles?

Most of the equipment I see in other retail businesses gets powered from wall warts/power bricks, USB or PoE. I looked online at some restaurant POS systems and found the same. Much of it is PoE to allow simple installation, data and power with 1 cable.

Basically most of the equipment out there doesn't connect to the EGC.
 