Isolated Equipment Grounding Conductors

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
They are all counted for box fill as the are all equipment grounding conductors, however if there are less than four total equipment grounding conductors of any type in the box, no additional volume is required. If you have more than four equipment grounding conductors of any type, an additional 1/4 volume is required for each conductor over four.
 