So this is a bit confusing and I can clarify anything, if asked.
I was called out to troubleshoot an outlet for a UPS system for cash registers at a grocery store that keeps turning off. Upon inspection of the panel it is a single phase 240v panel with an isolated ground, with multi wire branch circuits wired of a 3 phase panel. So instead of a two hot shared neutral for single phase, it’s wired with a 3 hot and shared neutral, which was the first issue I saw. All of the branch circuits go into one pipe and daisy chain through to where they land, there is 8 registers total. When I plugged in my plug tester it showed a missing ground, and somehow the conduit had been broken so we were called out to replace the flex and run new wire from the junction box.
When I shut the power off and checked continuity between the dirty ground and neutral it was at all 8 registers. But when I checked it between isolated ground and neutral/dirty ground it was reading continuity betweenat the 5th register but not the 6th, which tells me that it is disconnected/broken somehow. I then turned the power on and checked with my plug tester after removing the broken flex and wire and it read normal not missing a ground. I was also getting a very high resistance reading between isolated ground and neutral/dirty geound(which I assume was caused by induction). When I checked voltage there was not any voltage between isolated ground and neutral/dirty ground at register 5 but after that I was getting about 7v, but when I plugged in the UPS systems I was getting as high as 71v depending on which breakers were on, but typically about 32v
I didn’t check which phase the other breakers were on that was giving me the highest voltage reading(Didn’t think of it til after). I have some theories but not sure if there valid. I know what needs to be don’t to fix it, but could some explain the science behind it to me? Thank you
I was called out to troubleshoot an outlet for a UPS system for cash registers at a grocery store that keeps turning off. Upon inspection of the panel it is a single phase 240v panel with an isolated ground, with multi wire branch circuits wired of a 3 phase panel. So instead of a two hot shared neutral for single phase, it’s wired with a 3 hot and shared neutral, which was the first issue I saw. All of the branch circuits go into one pipe and daisy chain through to where they land, there is 8 registers total. When I plugged in my plug tester it showed a missing ground, and somehow the conduit had been broken so we were called out to replace the flex and run new wire from the junction box.
When I shut the power off and checked continuity between the dirty ground and neutral it was at all 8 registers. But when I checked it between isolated ground and neutral/dirty ground it was reading continuity betweenat the 5th register but not the 6th, which tells me that it is disconnected/broken somehow. I then turned the power on and checked with my plug tester after removing the broken flex and wire and it read normal not missing a ground. I was also getting a very high resistance reading between isolated ground and neutral/dirty geound(which I assume was caused by induction). When I checked voltage there was not any voltage between isolated ground and neutral/dirty ground at register 5 but after that I was getting about 7v, but when I plugged in the UPS systems I was getting as high as 71v depending on which breakers were on, but typically about 32v
I didn’t check which phase the other breakers were on that was giving me the highest voltage reading(Didn’t think of it til after). I have some theories but not sure if there valid. I know what needs to be don’t to fix it, but could some explain the science behind it to me? Thank you