Re: Isolated Ground Circuit
Bryan
I believe you are right, the NEC doesn't mandate where to terminate the IG conductor. Let me try the to explain why I believe it should be terminated at the separately derived bond in this case.
One feature of an IG is to limit neutral-ground noise. If the IG is tied to the location where neutral and ground are bonded, the n-g noise introduced at that point will be 0. If you land your IG conductor anywhere else, there is the likelihood of n-g noice being introduced.
Secondly, by running your ground past the source of the separately derived system in this case, and landing it on an upstream panel or service, you are creating the possibility of a larger than necessary n-g voltage at the IG receptacle.
For those reasons, I always require that the IG conductors be terminated at the location where neutral and ground are bonded for the system that the IG's are being installed
Jim T