More Detailed Info
More Detailed Info
The engineer came out to the project and made a report. In the report we were instructed to install piping and conductors in seperate conduits at computer panels.
Specification section 16120, page 3, line 31 thru 34 says we can install up to 6-#12AWG current carrying conductors per conduit. The plans do not indicate seperate conduits for computer runs.
The engineer responded as follows: Specification section 16110-2, lines 26-33, states to install complete, seperate conduit systems for all electrical systems on this project to include, but not limited to the following. New service entrance, electrical power and lighting feeders, electrical power and lighting circuits, control wiring furnished by this contractor, communication systems and other electrical systems. The drawings also indicate seperate home runs for clean and dirty power and is shown seperate in the wire routing on the drawings. Six conductors (3 circuits, 3 neutrals) may be combined in one conduit provided that all are either general purpose power or isolated ground power.
The engineer is hanging his hat on the "other electrical systems" as to mean the isolated ground circuits. We feel that the isolated ground circuits fall under the category of "electrical power and lighting circuits" and not an other electrical system.
The remark that the drawings indicate seperate conduit systems is misleading. The drawings indicate a home run arrow for each and every circuit. The drawings are diagramatic indicating which devices are served by which circuit.