Isolated ground conductor for noise purposes how do you size them?

depends on what you mean "for noise purposes". Chances are it will have no effect whatsoever on "noise" so the size just doesn't matter. If it is also serving as the branch or feeder circuit EGC than the normal EGC sizing rules apply.
 

Speedskater

Senior Member
Location
Cleveland, Ohio
Occupation
retired broadcast, audio and industrial R&D engineering
For an 'Isolated Ground' circuit, the EGC (Safety Ground) needs to be the same size (or larger) than the Hot & Neutral conductors.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
For an 'Isolated Ground' circuit, the EGC (Safety Ground) needs to be the same size (or larger) than the Hot & Neutral conductors.

What if the circuit is 50 amps and has #8 AWG conductors? 250.122 says that for that 50 amp circuit the EGC only needs to be #10.
 

kwired

Electron manager
Location
NE Nebraska
depends on what you mean "for noise purposes". Chances are it will have no effect whatsoever on "noise" so the size just doesn't matter. If it is also serving as the branch or feeder circuit EGC than the normal EGC sizing rules apply.
If it is truly "isolated" then there should be no connection to anything else at the feeder tier level, sizing to T250.122 and the branch circuit OCPD should be sufficient.
 