Isolated Ground Fill

Status
Not open for further replies.

dpenbert

Member
Location
Missouri
Article 314.16(A)(5) states that the equipment grounding conductor is counted once for box fill.
What if you have an isolated ground?

Thanks.
 
Re: Isolated Ground Fill

Read the section you posted it tells you what to do.


Part of 314.16(A)(5)
Where an additional set of equipment grounding conductors, as permitted by 250.146(D), is present in the box, an additional volume allowance shall be made based on the largest equipment grounding conductor in the additional set.
250.146(D) is about IGs
 