Our firm is doing the engineering for the main power to a maintenance shop complex on an industrial site. The rest of the building is being engineered by an A&E. The Owner recently contacted me saying that he is challenging the Isolated Ground design by the other Electrical Engineer. They ran a ground wire from an "instrument ground bus" (a copper ground bus bar mounted to the wall) to outside of the building and to a ground rod or possibly a triad. There is no connection to the main building ground loop. When the Owner challenged this, their response was that a Supplementary Grounding Electrode is allowed to not be connected to the main ground loop per NEC 250.54.
250.54 appears to me to be for lightning rod down-comer ground rods and not for actual equipment or building grounds. I guess the ground rods for portable generators would also fall under this section.
I am sure that the "isolated" or "instrument" ground must be connected to building ground. Ground must be Ground.
I would like to explain to the Owner why 250.54 does not apply. He is, I'm sure, going to require that they are connected but he would like a little code back up so he doesn't get hit with an "extra" since NEC compliance is part of the contract requirement.
250.54 appears to me to be for lightning rod down-comer ground rods and not for actual equipment or building grounds. I guess the ground rods for portable generators would also fall under this section.
I am sure that the "isolated" or "instrument" ground must be connected to building ground. Ground must be Ground.
I would like to explain to the Owner why 250.54 does not apply. He is, I'm sure, going to require that they are connected but he would like a little code back up so he doesn't get hit with an "extra" since NEC compliance is part of the contract requirement.