cole2915
New member
- Location
- Salt Lake City, UT, USA
I have a project that calls for the use of an isolated ground and this was missed. What's the thought on using 12/3 MC (blk,red, white, green) and using the green for the isolated ground back to the isolated ground bar in the panel and taping the red green for the use of bonding the box? I recognize there are some issues concerning proper marking of the conductors but this effectively would work.