Re: Isolated Ground Outlets (for computers) to eliminate Ha
Q1. Do you install Isolated Ground outlets ( for computers) to eliminate Harmonics? How does this work?
A1. IGR cannot possible eliminate harmonics, so it does not work. The only possible use for an IGR is a possible means of keeping common mode noise from entering the EGC circuit. It has no other purpose. Its effects in order are: 1. No effect. 2. Makes the problem worse. 3. Desired effect. Do not be confused about the IGR, it cannot remove or filter any common mode noise as there are no passive or active circuits involved.
Statement: ?Every Isolated Outlet, that I have ever installed, derived from a branch circuit that was feed from a panel with a separate isolated ground bar that eventually tied into the grounding electrode conductor.
Comment: this is one of the correct ways to derive a IGR
Q3 and Statement: ?I was told the only way to get a true Isolated ground was to drive a separate ground bar or create a "clean ground" through a Transformer. Is this true?
A3. Only a half truth and half myth. The myth part is driving a rod isolated from the ground electrode system would not comply with NEC requirements and would put personnel and the equipment at great danger. The truth part is transformers and some high-end UPS systems will remove or filter out common mode noise to the tune of 140 decibels (a ratio of 100,000,000,000,000:1) in some cases. These two systems are separately derived systems that establish a new N-G bond point. From this new point, a IGR can then be used to prevent common mode noise from entering the circuit via a single point ground. As long as the single point ground is not corrupted by comming in contact with any grounded objects, no common mode current can flow to develop a common mode voltage (noise)