Isolated ground receptacle

Status
Not open for further replies.

cppoly

Senior Member
Location
New York
Does the code require that if a isolated ground receptacle is installed it must go back to an isolated ground in a panel? Or would it be allowed to install the isolated ground and still run it back go the same ground on a panel. I know this defeats the purpose of isolated ground, but does the NEC allow it.
 
250.146(D) is written in a permissive context. You are allowed to run the isolated ground all the way back to the main panel without bonding it to any ground bar in any intermediate panel. But this is not a requirement.
 
Oops sorry let me ask the question again. Can an isolated ground receptacle have the IG conductor terminate in a non isolated ground buss bar in a panel?
 
If I'm not mistaken, if you are required to have IG receptacles then the isolated ground wire must stay isolated thru any sub-panel via isolated terminal bar and all the way back to the first means of disconnect where equipment grounds/neutrals/grounding electrode all tie together as well as your isolated ground wire.
 
Last edited:
The IG receptacle is not required. It appears a few of them were used just for the appearance of a special receptacle. I am confused because there is no isolated ground in the panel serving the area so I'm sure the IG conductor will be terminating on a normal grounding bar in the local panel along with other convenience receptacles. It defeats the purpose of the isolated ground receptacle. My best guess is that it gives the appearance of a IG receptacle and that was the intent only. Just wonder if code allows this.
 
The NEC doesn't really care where in the system that you terminate the IG. You could run a bonding jumper right to a grounded metal box.
 
Yea, I forgot it is not a NEC issue more so a performance issue which sounds like has been a farce and don't hear to much about IG recepts anymore.
 
The NEC doesn't really care where in the system that you terminate the IG. You could run a bonding jumper right to a grounded metal box.
I agree. The IG "exception" just permits the IGC to run through one or more metal enclosures and/or boxes without having to bond to the enclosure, box, or device(s) therein. The supply-end termination of an IGC is not required to be isolated from the EGC no matter where it is located.
 
Is the receptacle required to be IG?
If I'm not mistaken, if you are required to have IG receptacles then . . . .
Required by what? The NEC never requires IG. Perhaps the owner has a requirement for IG. In that case, if you don't keep the ground isolated all the way back to the main panel, then you will not have satisfied the owner's requirements. But you will not have violated any code requirement.
 