victor.cherkashi
Senior Member
- Location
- NYC, NY
Office space 3000 sq.ft., new tenant wants us to provide them isolated ground receptacles (furniture system workstations in open area).
I plan to run two EGC in conduit to workstations.
1. Green for regular purposes (grounding all metal parts, etc)
2. Green with yellow stripes from isolated ground terminal of furniture power whip to …? Here is question.
250.146(D) is connected to exception in 408.40. I can’t understand is it mandatory to connect the isolated EGC to applicable service or derived system, or it is just permitted (optional) ?
The office space is on 11th floor, the building distribution system is 120/208V 4000A, ConEdison service at basement. I don’t want to run one isolated EGC from 11th floor to service at basement just for this furniture system.
In case it is not mandatory (run the isolated EGC to the basement), I will connect the isolated EGC to grounding bus in tenant panel.