I know, I know; everyone has their opinion on isolated ground systems. Unfortunately, isolated ground systems are sometimes demanded by a client. Putting opinions aside, I am hoping you can help me settle a debate I am having with another engineer in my office.
See the attached file for a very simplified sketch I would like to use for this exercise. Also, lets assume:
His contention is that an IG conductor sized per T250.122 is too small to be protected from a ground fault by the primary OCPD and that the IG conductor should be the same size as the SSBJ, which is sized per T250.102(C)(1).
While his argument has merit, I cannot get around the fact that the NEC permits (not requires) IG conductor(s) to pass through panelboards, boxes, etc. all the way back to the source without making connections within the enclosures. Therefore, if the IG panel is full of 20 amp circuits, we would be permitted to run a separate #12 AWG IG conductor from each 20 amp circuit back to the transformer grounding connection point without any intermediate connections. We would never do this but the NEC would permit it.
I am hoping someone will be able to solve this debate. Thank you all in advance for your expertise!
Jason Rohe, P.E.
See the attached file for a very simplified sketch I would like to use for this exercise. Also, lets assume:
- Everything is completely code compliant with the only question centering around how to size the isolated ground.
- All connections from the transformer to the GEC are made at the transformer, not the first disconnecting means.
His contention is that an IG conductor sized per T250.122 is too small to be protected from a ground fault by the primary OCPD and that the IG conductor should be the same size as the SSBJ, which is sized per T250.102(C)(1).
While his argument has merit, I cannot get around the fact that the NEC permits (not requires) IG conductor(s) to pass through panelboards, boxes, etc. all the way back to the source without making connections within the enclosures. Therefore, if the IG panel is full of 20 amp circuits, we would be permitted to run a separate #12 AWG IG conductor from each 20 amp circuit back to the transformer grounding connection point without any intermediate connections. We would never do this but the NEC would permit it.
I am hoping someone will be able to solve this debate. Thank you all in advance for your expertise!