hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Please see attached. I have trough with two service disconnects and main grounding electrode system. One of service disconnect feeds Panel M which feeds isolated receptacles.
Panel M has isolated ground bus but instead of ruining the isolated equipment grounding conductor thru conduit thru panelboards eventually to terminate in equipment grounding bus in main service disconnect, their is grounding electrode conductor from Panel M isolated bus bar to main service grounding electrode system.
Questions:
1. I find this strange but not sure if a code would allow such grounding electrode connection? If not then I cannot spot right code section which would not allow this.
2. Assume that isolated ground bus bar is connected to equipment grounding bus bar Panel M which has EGC to main bonding jumper service disco then can the grounding electrode connection be made at Panel M isolated ground bus bar?
Panel M has isolated ground bus but instead of ruining the isolated equipment grounding conductor thru conduit thru panelboards eventually to terminate in equipment grounding bus in main service disconnect, their is grounding electrode conductor from Panel M isolated bus bar to main service grounding electrode system.
Questions:
1. I find this strange but not sure if a code would allow such grounding electrode connection? If not then I cannot spot right code section which would not allow this.
2. Assume that isolated ground bus bar is connected to equipment grounding bus bar Panel M which has EGC to main bonding jumper service disco then can the grounding electrode connection be made at Panel M isolated ground bus bar?