don_resqcapt19 said:
I argued this point with Mike Holt at the code changes seminar last fall.
He maintains that the words in bold below require that you run the isolated grounding conductor back to the point where the system or main bonding jumper is installed. I am not sure if I can stretch that back that far, but it does require, at a minimum, that the isolated grounding conductor be run to the panel where the branch circuit originates.
A section in need of revision.
The words in bold do not specify which circuit conductors. Are they Branch Circuit conductors or Feeder Circuit Conductors or both?
My problem with this section has always been these words:
......so as to terminate within the same building or structure directly at an equipment grounding conductor terminal of the applicable derived system or service.
The operative words above are".....so as to terminate....."
I take this to mean: Do what you have to in order to accomplish what follows. What follows is where they terminate.
There are two possible scenarios. One you have a step down xfmr and two you have a single voltage building.
Under scenario one, you can land it anywhere you want up to and including the xfmr. Key words in the Code are:
"...an equipment grounding conductor terminal of the applicable derived system...."
The definition of SDS includes premises wiring. That would lead me to say anywhere in the premises wiring system.
Under scenario two the building is served by a voltage that is not transformed. Here the key words are:
"...an equipment grounding conductor terminal of the applicable ...... service."
The definition of service limits us to the "The conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served."
That would lead me to say the Isolated Equipment Ground must terminate inside the Service Equipment.
Learned interpretations here on this forum as well as a CMP member Michael Johnston have all stated that you can terminate the Isolated Equipment Ground at any panel between the receptacle up to and including the xfmr or service.
I am of the same opinion. I do not insist the Isolated Equipment Ground go all the way back. I still get electricians and designers who want to take it to a ground rod or building steel.