The job specs require me to run an isolated ground from the panel to the 400 amp main disconnect which is approx 80' away. I am not to hip on running a ground through the existing energized conduit. Also I would need to change out the neutral bus in the disconnect because all the lugs are already used. Of course the neutral bus in directly behind A phase of the line. Does anyone have a good arguement I could use to avoid running the iso ground. By the way the iso ground is to be used for approx 4 cash register receptacles. Could I set an isolated ground bar in the panel and tie it to the neutral bar or would that be considered parallel paths which I know is a no no. Any ideas would be appreciated.