Re: Isolated ground
Hello-
You mentioned that "The IG was ran in a raceway with opposite phase circuits." This is not permitted because it will create noise on the IG conductor.
If you have access to a book published by EC&M magazine titled "Practical Guide to Quality Power for Sensitive Electronic Equipment" , on page 93 they list about 15 pitfalls for the installation of IG circuits.
The two that apply in this case:
"Running three insulated conductors but sharing the conduit with other circuits."
and
"Running the IG conductor to the grounding electrode through a raceway carrying a circuit feeding another load."
Also, take a look at the following document published by the Information Technology Industry Council:
http://www.itic.org/technical/ite_grnd.pdf
On page 6, paragraph #3:
"IT equipment should be powered from dedicated branch circuits wherever possible. A dedicated branch circuit not only has its own breaker, but also its own grounding conductor (ground) and grounded conductor (neutral) if used; neither of which is to be shared with other circuits."
If you have access to any IEEE Standards, take a look at IEEE 1100, Recommended Practice for Powering and Grounding Electronic Equipment. Chapter 9 gives details in the installation of IG and dedicated circuits. In section 9.3 they point out "Sharing common line, neutral, or grounding conductor paths by multiple electrical loads may produce unwanted interactions."
The National Electrical Manufacturers Association has an excellent publication in IG circuits for free download. Go to
www.nema.org and search for the "Application Guide for Isolated Ground Wiring Devices"- this is a 21 page .pdf file and discusses in greater detail what I have mentioned here.
I agree that you are measuring phantom voltages, but again my concern is that you will also have unwanted noise on this IG circuit due to induction from the other phase conductor(s).
Best wishes,
Mark