I agree, which I why I said that I would use a few as possible.Do whatever you want. Isn't going to amount to a hill of beans.
-Hal
I agree, which I why I said that I would use a few as possible.Do whatever you want. Isn't going to amount to a hill of beans.
-Hal
Agreed completely. But perception everything with this client. I could attempt to educate them but it would be futile.Do whatever you want. Isn't going to amount to a hill of beans.
-Hal
That would be fine.How about if we take one IG per circuit (to several receptacles) along with one EGC per circuit for along the same route from the panelboard ground bus?
Just give them orange IG receptacles if that's what they want, collect your check and walk away. Nobodies saying otherwise.But perception everything with this client. I could attempt to educate them but it would be futile.
Yes, you can run a EGC wire along the same route or just use the EMT.How about if we take one IG per circuit (to several receptacles) along with one EGC per circuit for along the same route from the panelboard ground bus?
You should give them what they're paying for even if it's basically useless. And if they were to test the IG system you would want to install something that at least meets the code minimum. We've had jobs where they came in after the IG system was installed and tested every IG receptacle for proper grounding. Then they removed the IG conductor at the X0 of the transformer and tested every IG receptacle to ensure that it was indeed isolated.Agreed completely. But perception everything with this client. I could attempt to educate them but it would be futile.
Did they provide specs/details on how what they considered the system would look like?You should give them what they're paying for even if it's basically useless. And if they were to test the IG system you would want to install something that at least meets the code minimum. We've had jobs where they came in after the IG system was installed and tested every IG receptacle for proper grounding. Then they removed the IG conductor at the X0 of the transformer and tested every IG receptacle to ensure that it was indeed isolated.
Yes we were given a design drawing and we were told that how they were going to test it (by removing the IG conductor). I think that this is actually from that job. The transformer fed a panel with an IG bus mounted on isolators.Did they provide specs/details on how what they considered the system would look like?
I would not like to be tested on something I was not told about.

hahaha good advice.Just give them orange IG receptacles if that's what they want, collect your check and walk away. Nobodies saying otherwise.
-Hal
In our case, thus far No, they have not provided that info.Did they provide specs/details on how what they considered the system would look like?
I would not like to be tested on something I was not told about.