I have a three phase piece of equipment whose vendor is requesting an "Isolated Ground". Old story...I know.
We provided an isolation transformer upstream of the equipment. We thought this would suffice, but the grounding conductor is still bonded to the secondary breaker right near the transformer and the disconnect near the equipment. The vendor does not like that and claims that the bonds at the breaker and disconnect box invalidate the isolation.
We suggested to bring another ground wire from the X0 terminal of the isolation transformer which he can use as the isolated ground for his electronics inside his equipment. He is fine with this, but also wants to disconnect the EGC and use the isolated ground to ground the enclosure.
I am 90% sure this is illegal, but I can't find anything in the code that would disallow it. Also, this would return all the fault current back to the source so I am not sure as to the reason why it would be illegal. Any ideas?
We provided an isolation transformer upstream of the equipment. We thought this would suffice, but the grounding conductor is still bonded to the secondary breaker right near the transformer and the disconnect near the equipment. The vendor does not like that and claims that the bonds at the breaker and disconnect box invalidate the isolation.
We suggested to bring another ground wire from the X0 terminal of the isolation transformer which he can use as the isolated ground for his electronics inside his equipment. He is fine with this, but also wants to disconnect the EGC and use the isolated ground to ground the enclosure.
I am 90% sure this is illegal, but I can't find anything in the code that would disallow it. Also, this would return all the fault current back to the source so I am not sure as to the reason why it would be illegal. Any ideas?