Isolated Grounding Receptacles

Status
Not open for further replies.

twbwfwforum

New member
Does code allow the installation of Isolated Grounding Receptacles if no true isolated grounding system exists. The use of the receptacles is to identify receptacles connected to a UPS system, utilization is for color only, and they are labeled as UPS receptacles. They are not wired as a isolated grounding receptacle
 
Re: Isolated Grounding Receptacles

Nope

406.2(D)(1)

I assume you jumpered the green screw to the box and have an equipment grounding conductor connected to the box. Not a safety issue really (if the above is done), but it is a violation.
 
Re: Isolated Grounding Receptacles

Why not install colored plates to designate the UPS receptacles? :confused:
 
Re: Isolated Grounding Receptacles

Or colored receptacles. I have used grey in the past for computer power.

Steve
 