Never thought I would be perplexed enough to ask something so silly here.
I am currently adding Data and receptacles for computers in a school. Specs call for isolated ground for each receptacle. Of course this was not found in the specs until wire is being pulled. But the question, Does each isolated ground count as 1 in each box, or are they considered part of the equipment grounding conductors (314.16(B)(1) Exception)where they only need to be counted once?
I am currently adding Data and receptacles for computers in a school. Specs call for isolated ground for each receptacle. Of course this was not found in the specs until wire is being pulled. But the question, Does each isolated ground count as 1 in each box, or are they considered part of the equipment grounding conductors (314.16(B)(1) Exception)where they only need to be counted once?