Allow me to jump in here folks. I have done a lot of work with IGR since the late 70?s and might be able to shine some light on the subject.
First, the IGR is only intended as a possible means of obtaining common-mode electrical-noise reduction on the circuit in which it is used. It has no other purpose. If the feed already has common-mode noise problems, the IGR cannot remove it, only an isolation device like a transformer or UPS can do that.
The IGR came about in 70/80?s time frame when banks and data processing started popping up. In those days all I/O port communication used an unbalanced form of communication like RS-232 where ground was used as a signal path. The common signal ground was connected to the EGC. As most of us know minute currents are injected into the EGC from nearby phase conductors which cause voltage differences along the EGC paths. These voltage differences are felt on the bit detectors and if large enough can cause errors in the detectors. Another example is hum on PA systems that is heard.
Well the days of RS-232 and all unbalanced signal transmission are gone. All modern communications today is balanced like Ethernet or optical, making IGR antiquated. I have not worked with any of the POS equipment and do not know why they are requiring IGR, maybe someone will enlighten me.
Someone mentioned IGR in telephone offices which is a horse of a different color. Telco use isolated single point ground for power supplies and equipment grounds. This is done for completely different reason, like eliminate out side fault currents (lightning, shorts) from flowing in the isolated ground plane. However I can tell from the description the poster stated is a misused application, is completely worthless, and likely to cause more problems than will be eliminated.
For example running the AC circuit from a remote source in PVC and isolating the box from the equipment rack. Once equipment is installed in the equipment rack uprights, plugged into the socked, the IGR is violated. This is not the correct use of the application.