Isolated phase parallel runs.

Status
Not open for further replies.

Spencen9ne

Member
Location
Vernal UT US
Utilizing 3 6" pvc conduits to a 3000A MDP. grouping parallel runs in an isolated phase per conduit manner. Planned on 9 800 CU runs using the 70 degree calc. Is it required to derate these conductors?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Why do would you want to do this iso-phase? Also a 90° C conductor van use it's 90° C ampacity for the derating calculation.
 