I'm specifying a 5kVA Isolated Power Panelboard for a hospital application and I have two options for the primary voltage; 120V or 208V (single phase of course). I want to go with the 208V, 1 phase but a colleague is telling me I should go with the 120V primary. He seems to think that a grounded voltage has some advantage over a line to line. I don't know why that would be the case.

Any thoughts?

thanks,

Mike
 

wirenut1980

Senior Member
Location
Plainfield, IN
I don't think it would matter either way since you would be running an equipment ground out with 120 V or 208 V. Plus in the isolation panelboard I think you are deriving a new neutral to ground bond anyways.
 

bob

Senior Member
Location
Alabama
What wirenut said. You do not need a neutral input to the transformer. You will establish a new neutral in the panel. Higher voltage smaller wire.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
bob said:
What wirenut said. You do not need a neutral input to the transformer. You will establish a new neutral in the panel. Higher voltage smaller wire.

There will be no neutral in the secondary of this system, it will be 120 v L-L. In my experience, the most common way (not always though) of feeding these panels / transformers are with L-N feeders, 120 or 277 volts, I don't really know why.

Roger
 

bob

Senior Member
Location
Alabama
roger said:
There will be no neutral in the secondary of this system, it will be 120 v L-L. Roger
I did not read any thing in the OP that indicated no neutral in the secondary.
I do not see where this fact has anything to do with whether the transformer is fed 208 or 120 volts.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
bob said:
I did not read any thing in the OP that indicated no neutral in the secondary.

Well, I'd bet that since this is a 5KVA Isolated Power Panel for a hospital, Mike is referring to a 517.160 application and there will be no neutral


bob said:
I do not see where this fact has anything to do with whether the transformer is fed 208 or 120 volts.
As I said, L-N is the most common way I see Isolated Power Systems fed but, I don't know why this is, there are times they are fed from a L-L source

Roger
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I'd feed it with the 208 volts.

If you use 120, you will have a 50 amp or larger breaker. That may be hard to coordinate with the next upstream feeder breaker, and/or the transformer inrush current.

Steve
 
D

Dickieboy

Guest
I believe the normal procedure in hospital applications are for line conditioners with integral isolation transformers with bonded neutral to ground secondary,,,,thus getting all noise out and away from the sensitive hospital equipment when needed,as to which voltage,you may need both depending on equipment to be used,208 is not to common for single phase users.

This post brings up a question as well, where are you getting 120V L to L for your primary? Is this a special set up for hospital distribution ?I'm not familiar with this source voltage or where you derive it.

dick
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Dickieboy said:
I believe the normal procedure in hospital applications are for line conditioners with integral isolation transformers with bonded neutral to ground secondary,,,,thus getting all noise out and away from the sensitive hospital equipment when needed,as to which voltage,you may need both depending on equipment to be used,208 is not to common for single phase users.

This post brings up a question as well, where are you getting 120V L to L for your primary? Is this a special set up for hospital distribution ?I'm not familiar with this source voltage or where you derive it.

dick

The OP transformer is for power supplies to operating rooms and therefore is concerned with isolating patients not equipment. There are very special rules in article 517.160.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Dickieboy said:
This post brings up a question as well, where are you getting 120V L to L for your primary? Is this a special set up for hospital distribution ?I'm not familiar with this source voltage or where you derive it.

dick

The 120 L-L (60-60) is the secondary voltage, the primary can be any voltage under 600 V, see 517.160(A)(2) The only reference to ground is through the Line Isolation Monitor. The combined ground and leakage currents must be less than .0006 amps in it's idle (no load all breakers off) state, the alarm threshold would 5ma.

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
steve66 said:
I'd feed it with the 208 volts.

If you use 120, you will have a 50 amp or larger breaker. That may be hard to coordinate with the next upstream feeder breaker, and/or the transformer inrush current.

Steve

Steve, I see many fed at 25 amp 277v, this saves space in the supply panel verses using double pole breakers for the feeders.

Roger
 

mshields

Senior Member
Location
Boston, MA
To Dick

To Dick

Dick - I am using a 208V single phase primary. Could use a 120V L-N primary? No I was not suggesting a 120V L-L primary.

Mike
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
roger said:
Steve, I see many fed at 25 amp 277v, this saves space in the supply panel verses using double pole breakers for the feeders.

Roger

Yes, I agree 277 would also be good. Probably even better since it may be eliminating other step-down transformers from the chain of possible failures.

But I think Mike only has 120 or 208 to choose from.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
My take on this is that the isolated secondary doesn't care whether the primary supply has a grounded conductor, I see no advantage to using a 120v circuit, and I concur with the higher voltage/lower current position, so I agree with using 208v.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
LarryFine said:
My take on this is that the isolated secondary doesn't care whether the primary supply has a grounded conductor,

Correct, it doesn't care or matter.

Roger
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
mshields said:
I'm specifying a 5kVA Isolated Power Panelboard for a hospital application and I have two options for the primary voltage; 120V or 208V (single phase of course). I want to go with the 208V, 1 phase but a colleague is telling me I should go with the 120V primary. He seems to think that a grounded voltage has some advantage over a line to line. I don't know why that would be the case.

Any thoughts?

thanks,

Mike
Use 208V single phase, and forget about it.
 