- New Jersey
- Occupation
- Electrician / Estimator
Good Morning,
Just looking for someone to double check me on this, and make sure I didn't miss anything. I am new to Isolated Power Panels, and would like to have my bases covered.
This is for an operating room, the previous electrician wired the Isolated Power Panels in HCF Rated MC. It has since failed their test, and the surgery center is looking to rip it all out and get it done correctly.
Circuits
www.pglifelink.com
Would I be able to use EMT with raintight fittings here? NEC 358.10 Uses permitted says yes I can use it in a wet location.
Or would I have to use Rigid because of a Article 517 code that I am not aware of?
The walls of this operating room are finished, we would run all the conduit exposed, and surface mounting it on the existing walls.
Unless there is a code reason not too? (With the exception that it might not look as clean)
The devices will be hospital grade duplex receptacles,
Because we are surface mounting the conduit, and this is a wet location.
I would assume I would need weather proof Boxes? weather proof covers? Or am I overthinking this?
Please let me know if there is anything else that I missed!
Just looking for someone to double check me on this, and make sure I didn't miss anything. I am new to Isolated Power Panels, and would like to have my bases covered.
This is for an operating room, the previous electrician wired the Isolated Power Panels in HCF Rated MC. It has since failed their test, and the surgery center is looking to rip it all out and get it done correctly.
Circuits
PG LifeLink standard Isolated Power Panels
Standard Isolated Power Panel Specifications | PG Lifelink

- Looks like I will need XHHW-2 Stranded Copper wire, in Brown, Orange, and Green.
- A total run of all circuits of 450Ft or less per Panel.
- No more then 6 wires in a 3/4" conduit (Does this mean two circuits? or Three not counting grounds? )
Conduit
It looks like operating rooms are considered "wet" locations. NFPA 6.3.2.3.4Would I be able to use EMT with raintight fittings here? NEC 358.10 Uses permitted says yes I can use it in a wet location.
Or would I have to use Rigid because of a Article 517 code that I am not aware of?
The walls of this operating room are finished, we would run all the conduit exposed, and surface mounting it on the existing walls.
Unless there is a code reason not too? (With the exception that it might not look as clean)
Devices
The devices will be hospital grade duplex receptacles,
Because we are surface mounting the conduit, and this is a wet location.
I would assume I would need weather proof Boxes? weather proof covers? Or am I overthinking this?
Please let me know if there is anything else that I missed!