Isolated receptacles

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
Can an isolated receptacle and regular receptacle be fed from the same 120V circuit? Both receptacles are NEMA 5-20R, i.e. isolated receptacle has both isolated and equipment ground wires while regular receptacle only has one equipment ground wire.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Yes they can but it kind of defeats the purpose of an IG system.

Not really. The separate IG conductor can pass through the regular receptacles and terminate in the ground screw of the IG receptacle. So the IG receptacle ground pin would have the isolated ground while the "regular" receptacle would get it's EG from normal means. This assumes you use IG cable with a separate green/yellow IG conductor.

But the question is would there be a problem with devices connected to the IG receptacle and regular receptacles because they share the same hot and neutral. My opinion is probably not, but I'm also of the opinion that IG receptacles have no use today too.

-Hal
 

anbm

Senior Member
Location
TX
Occupation
Designer
Not really. The separate IG conductor can pass through the regular receptacles and terminate in the ground screw of the IG receptacle. So the IG receptacle ground pin would have the isolated ground while the "regular" receptacle would get it's EG from normal means. This assumes you use IG cable with a separate green/yellow IG conductor.

But the question is would there be a problem with devices connected to the IG receptacle and regular receptacles because they share the same hot and neutral. My opinion is probably not, but I'm also of the opinion that IG receptacles have no use today too.

-Hal
Couldn’t think of any issues when they share same circuit but term “isolated” kind of warns me something… not sure.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Couldn’t think of any issues when they share same circuit but term “isolated” kind of warns me something… not sure.
In reality they are dedicated ground receptacles, even though our industry calls them isolated.
 