In my opinion, 250.104(C) can be interpreted to mean any portion of a building's framework that is metal. That is, the metal framework does not have to constitute the entire framework of the building (or structure, for that matter).I don't know. Art. 250.104 (C) talks of structural metal but it also states "to form a metal building frame" so I think not unless I am missing something. Of course any metal boxes will ground the ceiling via the egc but...
Many plans require that.In a building with block walls and a metal truss ceiling system is there any requirement to bond the structural ceiling ?
In my opinion, 250.104(C) can be interpreted to mean any portion of a building's framework that is metal. That is, the metal framework does not have to constitute the entire framework of the building (or structure, for that matter).
I would surely hate to bond every truss together in the entire building.![]()
250.104(C) requires exposed structural metal to be bonded if it is "likely" to become energized. It is a rare case where the exposed structural metal is likely to become energized. If we were still operation under the old code wording that required bonding where the metal "may" become energized, I would say that all of the metal would have to be bonded, but I don't see that as the case with the current code wording.
...and this subsection does not have the same allowance as in 250.104(B)
"The equipment grounding conductor fro the circuit that is liekly to energize the piping shall be permitted to serve as the bonding means."
Don
Would you say the steel would be 'likely to become energized' if there was a junction box with conductors that is supported to the steel?
or a piece of NM or MC strapped alongside it ?
Don't they usually have metal braces between them anyway?
Again what does likely mean. Think about the number of JB's out there and then think about how likely the steel is to become energized from the cable. Generally a short is made in a box or at some termination not because it is attached to metal.
Of course it can but is it likely to- IMO, No. This is the problem with the "term likely to".Dennis
Do you think the fault condition you mention could ever be transposed onto the steel the box is mounted to?
Of course it can but is it likely to- IMO, No. This is the problem with the "term likely to".
That is why I said the term stinks-- it leaves too much to subjectivity. Here is my thinking, if they wanted all the steel bonded then they should say that-- it leaves too much room for argument but of course, my ruling is the correct one. :grin:That is the key to this whole issue. It may not be to you, but what about some inspectors. Who is to say which person is correct?
Short of bare (uninsulated) conductors being run on insulators on the steel (and I am not even sure that this type of installation would be "likely" to energize the steel) I can't really think of any code compliant installation where I would say the steel is likely to become energized.Don
Would you say the steel would be 'likely to become energized' if there was a junction box with conductors that is supported to the steel?