Re: Isolated
IDF I believe stands for Intermediate Distribution Frame since he is talking about being in closets. It is a communications term used to describe a wiring distribution frame for telecom wiring such as CAT-X, coax, ABAM, etc..
If the ground bar is used for termination of cable protectors, cable shileds, or frame grounds, there should be no need to keep it isolated. It should go to the nearest availible ground electrode.
On the other hand, if it is used as a signal ground, it should be ran isolated back to the power source ground bar. The power source may or may not be the service entrance, it could be a DC plant, converter, isolation transformer, or sub-panel. In a plenum enviroment you can use a Teflon (TFE) insulated cable if you can afford it, or you can use conduit. If conduit is used you would need to isolate the conduit from incidental contact with building steel or concrete by mounting it on isolation cherries. Once the conduit is isolated you can bond the ground conductor at both ends to prevent choking and satisfy NEC requirements.
Dereck