I start fires
Member
- Location
- Litchfield, Connecticut, USA
So I have a customer with a residential 200A 120/240v single phase service. Panel has a 200A main breaker. This is the only service disconnect after the meter which is quite typical. Also as is expected, all branch circuit grounds and neutrals originate from a common bus within the panel. The customer wants to install a generator. One option would be to connect the generator by backfeeding through a breaker and installing one of those lockout devices that forces you to shut off the main disconnect before energizing the generator breaker. However if the customer wants an automatic backup generator I believe I would need to install a new 200A disconnect right after the meter connected to an automatic 200A transfer switch and then connect to the existing main panel. By code after the 1st disconnect, the neutral and ground must be permanently separated. I guess this requires me to install a separate ground bus in the main panel (which is basically impossible because of the lack of available space.) Also, there is no way the existing branch circuit neutral and ground wires are long enough to rearrange to complete the isolation. Bottom line, I don't see how isolating the ground and neutral is even remotely feasible in an existing panel with 40 or so breakers. I know that many homes have these auto-standby generators installed but I can't imagine the installer is going to reconfigure any ground or neutral conductors in an existing rat's nest panel. Am I correct? Are all of these transfer switch generator installs resulting in a code violation? Is there some type of bonding exemption for retroactively installing a transfer switch or am I missing something?