I could use some input regarding isolating a multi-tap current transformer on-the-run.
We are planning a job to replace a temperature gauge on a 35 / 4.16 kV transformer. As part of the transformer gauge, a heater element is fed from a Multi-Ratio Hot-Spot CT (X1 & X3 in use, X2/X4/X5 Open) internal to the transformer. To replace the gauge, we will need to disconnect the wires feeding the Hot-Spot CT wires to the heater element.
During the pre-job investigation, it was found that the factory had improperly installed the CT secondary wires and heater wires on the same side of the local shorting block, inside the transformer control cabinet.
Under normal circumstances we would jumper all windings to ground via the shorting block and move on with the work. However, due to the wires being installed on the same terminal of the shorting block, we will have to disconnect the X1 & X3 wires, open circuiting a portion of the Hot Spot CT Circuit.
The current plan is to the short X2 and X5 windings to ground at the local shorting block, done to provide a secondary loop for current to flow, and then to open the existing X1 and X3 circuit; avoiding hazardous voltage build-up on the X1 and X3 windings.
The concept that I am having trouble reconciling with is when the X1 wire is lifted on the shorting block, what is inhibiting the CT from building up voltage on the X1/X3 windings after X2 & X5 are shorted to ground?
I have found an old post from 2005 (Differential protection relay CT wiring question | Mike Holt's Forum), where rcwilson, discusses something similar.
*Picture for Reference Purposes
We are planning a job to replace a temperature gauge on a 35 / 4.16 kV transformer. As part of the transformer gauge, a heater element is fed from a Multi-Ratio Hot-Spot CT (X1 & X3 in use, X2/X4/X5 Open) internal to the transformer. To replace the gauge, we will need to disconnect the wires feeding the Hot-Spot CT wires to the heater element.
During the pre-job investigation, it was found that the factory had improperly installed the CT secondary wires and heater wires on the same side of the local shorting block, inside the transformer control cabinet.
Under normal circumstances we would jumper all windings to ground via the shorting block and move on with the work. However, due to the wires being installed on the same terminal of the shorting block, we will have to disconnect the X1 & X3 wires, open circuiting a portion of the Hot Spot CT Circuit.
The current plan is to the short X2 and X5 windings to ground at the local shorting block, done to provide a secondary loop for current to flow, and then to open the existing X1 and X3 circuit; avoiding hazardous voltage build-up on the X1 and X3 windings.
The concept that I am having trouble reconciling with is when the X1 wire is lifted on the shorting block, what is inhibiting the CT from building up voltage on the X1/X3 windings after X2 & X5 are shorted to ground?
I have found an old post from 2005 (Differential protection relay CT wiring question | Mike Holt's Forum), where rcwilson, discusses something similar.
*Picture for Reference Purposes