Existing street lights with metal poles are fed by a 120V, 2 wire source with no ground wire brought to light pole(s) creating an usafe situation to where the pole can be energized with 90-100 volts since a low impedance path doesn't exist to trip and OCPD.
Utility owns lights, so NESC applies. A possible solution was presented to install an isolation transformer (120-120V) within the pad-mount utility transformer to re-feed the existing lights utilizing the 2-wires to each pole, primary of isolation transformer would be fused. If a fault occurs to energize the pole in this case, no ground path would exist due to the ungrounded secondary of the isolation transformer, thereby increasing the safety to the public for the 1st fault.
I'm trying to build a case for reasons to justify not using an isolation transformer as a viable solution:1. Lighting surge may create an overvoltage to the isolation transformer secondary damaging the equipment, 2.NEC does not allow an isolation transformer for lighting circuits (only allowed for hospital receptacle ckts found in critical areas, recording audio studio equipment, and motor control circutis), and 3. I'd question the isolation transformer expected service life.
On a separate issue, I need to develop a workable solution to make it a safer installation than what presently exists and at the same time comply with NESC. With that being said, if anyone has suggestions/comments to either of the above last 2 paragraphs, I'd appreciate any comments.
Any viable solutions or other reasons to not install isolation transformers would be beneficial.
All new light pole standards include running 3 conductors that includes a separate ground to each pole and the ground conductor bonded to the pole. In lieu of retrofitting the older 2-wire installation to bring up to the new standards, do other options exist and still meet code. I'm not sold on the isolation transformer as a solution at this point, but would like to cite code reasons not to go with the isolation transformer idea.
Thanks.
Existing street lights with metal poles are fed by a 120V, 2 wire source with no ground wire brought to light pole(s) creating an usafe situation to where the pole can be energized with 90-100 volts since a low impedance path doesn't exist to trip and OCPD.
Utility owns lights, so NESC applies. A possible solution was presented to install an isolation transformer (120-120V) within the pad-mount utility transformer to re-feed the existing lights utilizing the 2-wires to each pole, primary of isolation transformer would be fused. If a fault occurs to energize the pole in this case, no ground path would exist due to the ungrounded secondary of the isolation transformer, thereby increasing the safety to the public for the 1st fault.
I'm trying to build a case for reasons to justify not using an isolation transformer as a viable solution:1. Lighting surge may create an overvoltage to the isolation transformer secondary damaging the equipment, 2.NEC does not allow an isolation transformer for lighting circuits (only allowed for hospital receptacle ckts found in critical areas, recording audio studio equipment, and motor control circutis), and 3. I'd question the isolation transformer expected service life.
On a separate issue, I need to develop a workable solution to make it a safer installation than what presently exists and at the same time comply with NESC. With that being said, if anyone has suggestions/comments to either of the above last 2 paragraphs, I'd appreciate any comments.
Any viable solutions or other reasons to not install isolation transformers would be beneficial.
All new light pole standards include running 3 conductors that includes a separate ground to each pole and the ground conductor bonded to the pole. In lieu of retrofitting the older 2-wire installation to bring up to the new standards, do other options exist and still meet code. I'm not sold on the isolation transformer as a solution at this point, but would like to cite code reasons not to go with the isolation transformer idea.
Thanks.