Leyden Jar
New User
- ME
- Self Employed
Condition: In order to power a transfer switch (6 circuit 120V) through a 60 amp sub panel. A floating neutral current must be enabled. In place of a generator is instead a connection to an alternative 120v 15 amp power source dedicated bonded neutral. (Outdoor GFCI 15 amp outlet via extension cord)
Solution: Convert bonded neutral to floating neutral using an isolation transformer. (example: Isolation Transformer)
Problem: When utility power is restored then the house current is effectively bonded neutral.
Equipment: Transfer switch is a UTS6 with many features and has capacity to cut off when power is restored. Only, as an assurance and a certain safe guard there are three cut off switches. 1) Simply, toggle off the 60 amp breaker to sub panel in Main. 2) Switch the Main panel to off. 3) Disconnect from the utility by switching off emergency cut off switch below the meter and above the 100 amp outside service entrance to the Main panel.
Apparatus: Isolation transformers with (Faraday Cage) Faraday Shields are used to produce a magnetic field that charges the coils from the input side coil to the output side/secondary coil. In this condition the floating neutral condition is derived.
Questions: What happens to this condition when the neutral and ground become bonded from within the floating circuit pathway as to when the house current is restored? Does that cause a distortion to the isolation transformer? If, 1) Only the sub panel breaker is switched off. 2) The Main panel is switched off. 3) The disconnect from the utility is used to cut off from the Main.
Thanks in advance for your help and considerations.
Leyden Jar
Leyden Jar