We are installing a new isolation transformer upstream of an existing UPS on a 480V system which is being converted to an HRG system. The current configuration on a solidly grounded system has an ATS fed from two upstream feeders with the load side of the ATS feeding into the existing UPS. The existing UPS does not have input OCPD's but rather has a 1200A input switch as well as a 1200A bypass switch with a jumper between these two switches at the input of the UPS.
We are now installing a new 112.5kVA 480D-480Y transformer between the existing ATS and UPS. We plan on replacing the two upstream feeder circuits which feed the ATS with 150A breakers which are within 125% of primary FLA.
Because the primary protection is within 125% of transformer FLA there is no secondary protection required for the transformer itself. However to my knowledge there will still be OCPD required for the for the transformers secondary #1/0 cables between the transformer and UPS. Because the UPS does not have input OCPD's do we need to add some sort of OCPD between transformer and UPS or is there a provision in code that allows for no OCPD required at UPS for protection of these secondary cables?