Isolation Transformer question

Status
Not open for further replies.
My guess is that the supply grounding would be specified in the standard you are testing to.

Either they will require a solidly grounded source to mimic the environment you are testing for, or they will require something like an ungrounded system for test safety, or possibly a resistance grounded system with instrumentation on the grounding resistor.

Perhaps someone else here is familiar with the test.

-Jon
 