Not sure I understand your question, but an isolation or any transformer for that matter, creates a new ground reference point free of current (noise). So I think the answer to your question is NO.awc said:Ok, one more question. In an isolation transformer, the ground is passed through from primary source,correct?
dereckbc said:If the noise you refer too is Common Mode Noise absoltutely YES. And with a special ferroresonat isolation transformer will correct voltage fluctuations.
Lxnxjxhx said:Here's a link but I couldn't easily get a data sheet for one of these. Having numbers is better than saying "superior" and "noise reduction".
http://www.tripplite.com/products/conditioners/transformers.cfm
I would say "removes" should be "weakens."
It may or may not and depends on what you are talking about. For example if you are talking high frequency noise using a shields and ferroresonant tunning it will virtually eliminate all HF noise, but for common mode noise, there is nothing better than a transformer for the money. Otherwise you would use a dual conversion UPS to remove both common and normal modes.ELA said:What if it is differential mode noise :smile:
Sorry but that is inaccurate. The main function of an isolation transformer is establishing a new power ground reference point close to the point of use. This greatly reduces (up to 140 db) the problem of common-mode noise induced through "ground-loops" or multiple-current paths in the ground circuit upstream of the newly established reference ground point.ELA said:As far as the ground it will not help clean up ground noise if the ground is bonded to the secondary.
dereckbc said:Sorry but that is inaccurate. The main function of an isolation transformer is establishing a new power ground reference point close to the point of use. This greatly reduces (up to 140 db) the problem of common-mode noise induced through "ground-loops" or multiple-current paths in the ground circuit upstream of the newly established reference ground point.
There is no code compliant way to accomplish that. The primary and secondary equipment grounds must both be connected to the transformer enclosure.ELA said:An isolation transformer can provide a new reference point. It can also be clean if the incoming ground is isolated from the outlet ground.
don_resqcapt19 said:There is no code compliant way to accomplish that. The primary and secondary equipment grounds must both be connected to the transformer enclosure.
I don't believe in magic.dereckbc said:An isolation transformer forms a new ground point, what ever is upstram is never seen by the equipment with respect to ground once the new reference point is established. So yes it magically makes the ground noise dissapear.
.
AWC you are asking good question and no reason to apologize. Before you read my answer do yourself a favor and read 250.30(4) as it will tell you your options.awc said:Ok, I believe my question is now answered. The bonding point on the isolation transformer will form a new grounding point and help reduce some of the specific noises? :-? So now would you bond to building steel as you would any other transformer. Sorry guys but i'm new to all this so I apologize if some of my questions are a bit annoying.