Isolation Transformers and Double Tapping

Status
Not open for further replies.

aeagle

Member
Location
Virginia
Occupation
Electrical Engineer
For an amphitheater I have a 200A and 400A 208/120V 3Ø company switches and they want a single isolation transformer for these. 208V is our primary voltage. Can I use a single 225kVA 208-208/120V isolation transformer and double tap it to serve both of the company switches?
 
For an amphitheater I have a 200A and 400A 208/120V 3Ø company switches and they want a single isolation transformer for these. 208V is our primary voltage. Can I use a single 225kVA 208-208/120V isolation transformer and double tap it to serve both of the company switches?
A few questions.

What do you mean by "company switch".?

What do you mean by "double tap"?

What do you mean by "isolation transformer"? I think the transformer would need to have its secondary grounded to a GES to meet code. It would also need to be bonded.

If you need the full 600 Amps, a 225 kVA transformer at 208 V 3/phase would be 625 Amps, so it can certainly handle the load.
 
"Company switch" is where a traveling show connects their own power distribution.
Yes, one transformer can supply two disconnects provided you abide by tap and overcurrent-protection rules.
If they actually want a transformer there (why???), they as above it needs to be properly bonded/etc as an SDS.
 