Himooo ? When you made your inquiry the second time you identified harmonics (very ubiquitous term) but you did not identify your loads. You should throw some application details in because having read through this thread I see you have drawn some big guns out. What are you working on? Single/Three phase? What?s your Primary/Secondary voltage? Load type(s) - Motor/lighting/other?
The commentary on triplens by our moderator is great (thank you) so let me create a scenario with two identical loads that generate harmonic "current" multiples of 6+/-1 on the AC supply, one with and one without an isolation transformer:
1000HP pumping requirement
Available power is 3P, 480V
Process allows for and plumbers are savvy enough to build a system with 2 x 500HP pumps
2 x 500HP VFDS with 6 pulse front ends are selected
A 480/480V isolation transformer is connected ahead of one VFD. A line reactor with similar impedance is connected in front of the other
Merits:
Pumps & Motor availability fit schedule, subsequent service improved for I hope obvious reasons
Power conductors, conduits and related components far more manageable
We reduced the available short circuit current
Running at reduced capacity on one pump should the other fail
Isolation transformer phase shifts input power 30 degrees to one VFD cancelling the 5, 7, 17, 19, 29, 31, etc harmonic currents generated on the AC supply when running at the same load as the other VFD.
Not one loss inserting high priced harmonic filter was required
And so on ........
jcormack Bob: you could add an item 7 to your list, something about dI/dT, because after my family, dogs & golf, inductors are my favourite thing on this planet.