(work was done by a former electrical contractor)
I have a rooftop panel - 3ph 208v 200A, on the panel I have a 2P 100A breaker feeding a 25kva transformer with a secondary output voltage of 240, this leads to a 2P 60A GFCI breaker. The secondary load is a jacuzzi 230v 42A load.
Problems - Transformer is hot to the touch, spa pumps working (2 motors each 230v 11A) but no heat,
Q- Is the transformer big enought to handle this load?
Q- When calculating a voltage increase (208v primary to 240v secondary) are the calculations different than as stated below?
Multiply KW by 1000/voltage and then by power factor.
25kw x 4.16(1000/240) = 104 x .90 = 93.6 Amps -- Is this correct?