IT delta

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
On the spec sheet for the SolarEdge SE 120K I see:
Supported Grids WYE: TN-C, TN-S, TN-C-S, TT, IT; Delta: IT

What does the "IT" mean?
 
As I understand it an IT system is a what we call a ungrounded system (the I part) typically with ground detectors and or residual current detectors. The 'T' indicates that there is an equipment grounding conductor that goes back to a GEC and the ground detectors.
 
As I understand it an IT system is a what we call a ungrounded system (the I part) typically with ground detectors and or residual current detectors. The 'T' indicates that there is an equipment grounding conductor that goes back to a GEC and the ground detectors.
That is consistent what what I have been able to find out as well. Thanks!
 