This was brought to my attention the other day from a contractor;
3M Stak-It SI-1, Cable Stacker- these are sold in a red plastic bag of 25.
Flat NM cable:
1-8* each 14-2 W/G (15 Amperes)
1-4 each 12-2 W/G (20 Amperes)
1-4 each 10-2 W/G (30 Amperes)
* When placing 5-8 14-2 W/G into the 3M Cable Stacker, derating of the conductor ampacity should be considered.
Two questions arise from the above quote from the package.
1. If placing 5-8 14-2 NM cables, does this mean that derating is required or suggested?
2. Does this also mean that 3-wire NM is not permitted as per listing to be installed with the stackers?
One other question.
Do any other inspectors here permit the use of the Stacker for installing the cable on studs that are less than 2x4 in dimension, to satisfy 300.4(D)?
(this would obviously require the installer to modify the Stacker to fit the smaller dimension stud)
Thanks
Pierre
3M Stak-It SI-1, Cable Stacker- these are sold in a red plastic bag of 25.
Flat NM cable:
1-8* each 14-2 W/G (15 Amperes)
1-4 each 12-2 W/G (20 Amperes)
1-4 each 10-2 W/G (30 Amperes)
* When placing 5-8 14-2 W/G into the 3M Cable Stacker, derating of the conductor ampacity should be considered.
Two questions arise from the above quote from the package.
1. If placing 5-8 14-2 NM cables, does this mean that derating is required or suggested?
2. Does this also mean that 3-wire NM is not permitted as per listing to be installed with the stackers?
One other question.
Do any other inspectors here permit the use of the Stacker for installing the cable on studs that are less than 2x4 in dimension, to satisfy 300.4(D)?
(this would obviously require the installer to modify the Stacker to fit the smaller dimension stud)
Thanks
Pierre