Here is the situation:
Cable tray in IT room which falls under all requirements of 645.2, run from loadcenter to above IT equipment racks. 12/3 type TC cable, not exceeding 15' in length per 645.5(b)2, marked "TC/CDRS GY/LE" can't find those letters in art.400, anyone know what they mean? Cable comes out of tray approx 12" to a 20A twistlock female cord cap to connect to the IT equip. Inspector won't pass citing "fixed equip." needs to be hardwired or a box w/ recp. on the tray. I interpret 645.5(b)2 to allow this install. Any opinions or code ref.'s to back this up would be appreciated, as I plan to call him on this.
Cable tray in IT room which falls under all requirements of 645.2, run from loadcenter to above IT equipment racks. 12/3 type TC cable, not exceeding 15' in length per 645.5(b)2, marked "TC/CDRS GY/LE" can't find those letters in art.400, anyone know what they mean? Cable comes out of tray approx 12" to a 20A twistlock female cord cap to connect to the IT equip. Inspector won't pass citing "fixed equip." needs to be hardwired or a box w/ recp. on the tray. I interpret 645.5(b)2 to allow this install. Any opinions or code ref.'s to back this up would be appreciated, as I plan to call him on this.